Demo Application - Subscription failed: AccessDenied
24 Jan 2022 15:13 #10565 by roburtm
Yes, we only found a solution for Titanium OPC.
As you can see in previous posts, QuickOpc fails to subscribe with AccessDenied exceptions.
24 Jan 2022 13:04 #10564 by support
thank you for update.
Are you saying that you have found a solution with "Titanium OPC" only, or that you also have found some solution with QuickOPC?
Notes:
1. QuickOPC already calls CoInitializeSecurity, and its arguments can be influenced by the parameters I have provided.
2. Due to some changes Microsoft is doing (support.microsoft.com/en-us/topic/kb5004442-manage-changes-f...52-c141-43d2-941e-37ed901c769c ) there will probably be more options to tweak, in QuickOPC 2022.1 version.
21 Jan 2022 11:22 #10563 by roburtm
We found a solution for the problem - kind of.
We also tried the open source OPC library "Titanium OPC" which exactly had the same problem when not calling the "Bootstrapper.Intialize()" method, which is equivalent to calling "CoInitializeSecurity".
17 Jan 2022 08:23 #10540 by support
Unfortunately there isn't much else, and nothing specifically targeted.
Possibly revert the changes you made, and then try different settings of
  • EasyDAClient.ClientParameters.UseCustomSecurity
  • EasyDAClient.ClientParameters.TurnOffActivationSecurity
  • EasyDAClient.ClientParameters.TurnOffCallSecurity
(can only be done *once* in the program run, before any OPC operation is attempted)
Related info:
- www.opclabs.com/forum/connections-reconnections-com-dcom/124...ng-to-remote-machines-via-code
- kb.opclabs.com/COM_settings_in_OPC_Classic_client_components
And, combine it with further DCOM tweaking... Sorry, I have nothing better.
07 Jan 2022 07:53 #10533 by roburtm
Thank you for the suggestion. Today, we tried the managed implementation but neither the Read, nor the Subscribe do work.
See the attached screenshots for details.
Anything else I can try?
05 Jan 2022 09:55 #10530 by support
can you please unpack the attached file, place the resulting appsettings.json file alongside the EasyOpcNetDemo.exe , and retest?
Explanation: QuickOPC contains two low-level implementations of OPC DA client code. Sometimes the default implementation differs in DCOM-related settings. This configuration file tells QuickOPC to use a second implementation, written completely in managed code (the default one is a mixed mode C++/CLR).
File Name: Appsetting...ssic.zip
File Size:0 KB
04 Jan 2022 10:51 #10529 by roburtm
Thank you for your quick reply.
Reading/writing works in the QuickOPC Demo application. Only "subscribe" fails with the given exception.
04 Jan 2022 09:54 #10528 by support
Dear Sir/Madam,
Can you please tell me whether Read works in the QuickOPC demo application? If not, what error does it give?
Note: Sometimes, DCOM settings that work with one client do not work with other. I think you are already observing this, because the Async reads should work (in QuickClient), and the fact that they don't may be related to the fact that essentially the same mechanism is used for subscriptions as well as for async methods.
I do have some guidance/recommendations but that will depend on your answer to the question at the beginning.
03 Jan 2022 14:04 #10527 by roburtm
we are evaluating EasyOPC.NET to access data on an OPC DA server at a customer site with .NET.
The DCOM configuration *should* be okay, since we instructed the opc server manufacturer to configure the server/client properly.
We tested the configuration using the "OPCExpert" Tool, as well as the "Kepware OPC QuickClient" and the connection and also subscriptions are working.
The "OPCExpert" Tool works 100%, the QuickClient looks like it works, but we're not 100% sure if it uses subscriptions. Async Reads do not work there, though.
Then, we were installing the "EasyOPC.NET Demo" and connecting/reading works, but subscribing to a value does not work. Of course we're testing on the same machine with the exact same login.
Please see the following screenshot. (On the right side, you can see the "OPCExpert" Tool with its log messages).
How can we diagnose further why EasyOPC.NET cannot subscribe?
Time to create page: 0.079 seconds
