08 Sep 2015 13:48 #3555 by support
We do not limit this on client side. The practical limits will come "from other sides" - wheny ou create too many connections, it will eat memory, it will eat CPU, it may be too many for the target computer, it will become inefficient. It is impossible to give a number or a formula.
  • saravana48
08 Sep 2015 13:06 #3554 by saravana48
If seperate connection will create to connect each different remote server, then what is the maximum limit for connection with the OPC server from a QuickOPC client application?
08 Sep 2015 12:27 #3553 by support
Each different remote server will have one connection.
That's kind of obvious in the OPC world: a connection (represented by DCOM OPCServer and the stuff that gets created from it) is a two-ended "pipe" between a client and a server. There cannot be a pipe that connects one client to multiple servers.
  • saravana48
08 Sep 2015 12:19 #3552 by saravana48
Thanks for the response.
I am using 10 EasyDAClient object to subscribe from 10 OPC server(each OPC server located in different machine) with the default Isolated property(False) in a client application.
In this case, will there be one (shared) connection establish to connect all the OPC server? orelse will it create 10 different connection?
08 Sep 2015 12:04 #3551 by support
Whether a TOP server itself has a limitation, I do not know.
As to the connections on the client side: Each process (app) that uses QuickOPC assemblies (more precisely, each app domain, but usually there is just one app domain in a process), has its own connections.
And, all the EasyDAClient objects in one app domain will normally create just one (shared) connection to any given OPC server - no matter how many of these EasyDAClient objects you use. You can force a creation of separate connections by setting the Isolated property on each such EasyDAClient object to 'true'. Then, separate connections will be created. There is practical hard-coded limit on the number of such connections to be created on our side (QuickOPC), however it is advised that unless there is true reason, you use just one connection, or a handful of them, but not too many.
  • saravana48
08 Sep 2015 11:38 - 08 Sep 2015 11:44 #3550 by saravana48
Is there any restriction on number of connection to a server(TOP server)?
Last edit: 08 Sep 2015 11:44 by saravana48.
08 Sep 2015 11:10 - 08 Sep 2015 11:11 #3549 by support
Thank you for update.
- Settings made in one application do not affect other applications.
- Increasing the hold period should not negatively affect the performance of Top Server - in fact, it can be expected that it'll have a positive effect. The reason why the default is relatively short is that some servers need to be disconnected from all clients (and shut down) in order to update their address space, if it's dynamic.
- The connections are per server & per machine. Attempting to use the "subscription hold" technique to a local server will not keep the remote server connected.
- I can only guarantee the "subscription hold" technique with the latest QuickOPC version (5.34). Some older versions have functioned differently in this respect; and, we do not support them.
- If you have purchased a license while 5.3x (e.g. 5.30 or 5.31 etc.) was the current version, then you are automatically licensed to all 5.3x version (including the current version 5.34) and do not have to pay anything.
And, last of all, it should be said that it is still weird why the connection should take so long (longer than the default of 1 minute). Anything described above is basically just a workaround, but does not address this issue. It is, however, likely, that the delay is on the server side.
Last edit: 08 Sep 2015 11:11 by support.
  • saravana48
08 Sep 2015 05:21 #3548 by saravana48
I have tried both subscription with server and configuring HoldPeriods.TopicWrite to maintain the open connection with the server. But the subscription mechanism throws the error 'Cannot connect Data Access client (timeout)' occasionally, while configuring the HoldPeriods.TopicWrite works.
I have set the HoldPeriods value as 30 minutes. The tag/item successfully writes if the subsequent request arrives before 30 minutes(HoldPeriods value), but the write request which arrives after 30 minutes throws the timeout error. So now I increased the HoldPeriods value to 60 minutes.
I have another 3 VB.NET client application running in the same machine which subscripes arround 150 tags/items and writes to 250 tags/items in same Top server.
1)Will increasing the HoldPeriods value affect the subscription and write operation in other applications?
2)Will increasing the HoldPeriods value affect the performance of the Top Server?
  • saravana48
07 Sep 2015 11:16 #3544 by saravana48
The subscription starts at the beginning of the application and unsubscribe while closing the application. The application running in 24X7.
Note: I made subscription to remote server, while the writing operation performed to the local server(where the client application running). Both subscription and write operation using different EasyDAClient object.
The problem is in establishing connection with the server within the configured timeout during read/write operation. Am I right? If so, then we have to maintain an open connection with the local server(timeout error raising server).
Can we maintain a open connection by any one of the following? If so then which one is feasible?
  • subscribing a tag/item from the server(timeout error raising server). As far as I know the subscription maintains the open connection with the server
  • configuring HoldPeriods.TopicWrite.
07 Sep 2015 09:22 #3543 by support
Thank you for the answers. I am sorry - one more question: How is the subscription used? Is it e.g. so that you subscribe t something at the very beginning, and then keep it subscribed for long time, or do the subscriptions also change or go away?
The reason I am asking is because the error you are getting has to do with "initial" connection to the OPC server. But the connection should be kept open as long as there is any subscription in effect. However the matter is a bit more complicated, so I need to gather the facts first.
Anyway, the basic two suggestions to start with are as follows:
1. Increase the "hold period". For individual Reads or Writes, this is the amount of time for which the connection is kept open after the operation. If the problem is in establishing the connection, then having a long hold period would mean that the connection will stay open and will not have to be reestablished again. It can be e.g. a value around half an hour easily, i.e. 30*60*1000 milliseconds. On the EasyDAClient object, it is in HoldPeriods.TopicWrite property.
2. Upgrade to recent version (5.34 as of now).