Limitations of live mappings?
26 Jan 2017 05:51 #4893 by support
Hello:
-subscribe to the update failure event
Yes
-mapping the a similiar class with a different mapping kind (exception, error code, etc.) to the struct on the server where the data type should match the mapping kind?
Not precisely. Not a separate class. Just pick one of the properties that do not update, and add an extra property to the same class, next to it. E.g. besides having "public double Input1 { get; set; }, add also "public Exception Input1Exception { get; set; }". And use "[UAData(Kind = UADataMappingKind.Exception)]" as you have in your example. BUT, everything else (attribute-wise) should be the same as on the original property. So if your original property for subscriptions and reads, the exception one should be too - so that you can diagnose the subscription/read issues.
The following user(s) said Thank You: Captain_Dash
25 Jan 2017 20:56 #4892 by Captain_Dash
Just for clarification, my next steps should be:
-mapping the a similiar class with a different mapping kind (exception, error code, etc.) to the struct on the server where the data type should match the mapping kind? --> do you have an example for this?
Do you mean something like this?
        [UANode, UAData(Operations = UADataMappingOperations.Write, Kind = UADataMappingKind.Exception)]    // not readable
        public Exception Input1 { get; set; }
25 Jan 2017 18:28 #4891 by support
There is no such limitation in the Live Mapping.
First thing to do in the troubleshooting is to make sure you have all information about possible errors that might be occurring. Please read "Error Handling in the Mapper Object": opclabs.doc-that.com/files/onlinedocs/QuickOpc/Latest/User%2...n%20the%20Mapper%20Object.html .
Make sure you have some way to detect all these kinds of errors. Specifically, make sure you also add some mapping with Kind of Exception (or ErrorMessage or ErrorCode) (opclabs.doc-that.com/files/onlinedocs/QuickOpc/Latest/User%2...rame.html#Mapping%20Kinds.html ), so that you can discover the issues described under letter (D). But other possible causes, e.g. (C), cannot be ruled out either, so please have some handling for them too.
25 Jan 2017 15:19 #4890 by Captain_Dash
I tried to use the live mapping feature for struct on the opc server. I created a class which is similiar to the struct and equipped the class with the attributes of your live mapping feature. Of this class I created 3 instances because I need to map each class to a different instance of the struct on the server. In the first place I started to map this class and everything works fine, so added the second, still everything is fine. I am getting the changes from the server, so the subscription is working, i call the read method and all values are read. But if I add the 3rd instance nothing is working anymore, neither the subscription nor the reading of the values. If I only run the 3rd instance alone everything is working again.
Why is this happening? Are there any limitations in the count of the mappings?
    [UANamespace("XXXANamespaceXXX")]
    [UAType]
    public class MotionAxis : BindableBase
        private Meta metaInfo = new Meta();
        [UANode(BrowsePath = ".meta")]
        public Meta MetaInfo { get { return metaInfo; } set { SetProperty(ref metaInfo, value); } }
        private Control control = new Control();
        [UANode(BrowsePath = ".control")]
        public Control Control { get { return control; } set { SetProperty(ref control, value); } }
    [UAType]
    public class Control : BindableBase
        # region private fields
        private byte mode;
        private double setPosition;
        private double setVelocity;
        private bool power;
        private bool execute;
        private bool reset;
        private byte readDigitalInputs;
        private int readAnalogInputs;
        private double currentPosition;
        private bool done;
        private bool busy;
        private bool error;
        private uint errorCode;
        private byte writeDigitalOutputs;
        private ushort controlword;
        private int targetPos;
        private byte modeOfOperation;
        private byte digitalIn;
        private byte digitalOut;
        private int analogIn;
        private int targetVelocity;
        private int profileVelocity;
        private int actualVelocity;
        private ushort statusword;
        private int actualPos;
        private short hwErrorcode;
        private int univar0;
        private int univar1;
        #endregion
        /// <summary>
        /// Gets or sets the value of Mode.
        /// </summary>
        [UANode(BrowsePath = ".Mode"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public byte Mode
            get { return mode; }
            set { SetProperty(ref mode, value); }
        /// <summary>
        /// Gets or sets the value of SetPosition.
        /// </summary>
        [UANode(BrowsePath = ".Set_position"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public double SetPosition
            get { return setPosition; }
            set { SetProperty(ref setPosition, value); }
        /// <summary>
        /// Gets or sets the value of Set_velocity.
        /// </summary>
        [UANode(BrowsePath = ".Set_velocitiy"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public double SetVelocity
            get { return setVelocity; }
            set { SetProperty(ref setVelocity, value); }
        /// <summary>
        /// Gets or sets the value of Power.
        /// </summary>
        [UANode(BrowsePath = ".Power"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public bool Power
            get { return power; }
            set { SetProperty(ref power, value); }
        /// <summary>
        /// Gets or sets the value of Execute.
        /// </summary>
        [UANode(BrowsePath = ".Execute"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public bool Execute
            get { return execute; }
            set { SetProperty(ref execute, value); }
        /// <summary>
        /// Gets or sets the value of Reset.
        /// </summary>
        [UANode(BrowsePath = ".Reset"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public bool Reset
            get { return reset; }
            set { SetProperty(ref reset, value); }
        /// <summary>
        /// Gets or sets the value of Read_digital_inputs.
        /// </summary>
        [UANode(BrowsePath = ".Read_digital_inputs"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public byte ReadDigitalInputs
            get { return readDigitalInputs; }
            set { SetProperty(ref readDigitalInputs, value); }
        /// <summary>
        /// Gets or sets the value of Read_analog_inputs.
        /// </summary>
        [UANode(BrowsePath = ".Read_analog_inputs"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public int ReadAnalogInputs
            get { return readAnalogInputs; }
            set { SetProperty(ref readAnalogInputs, value); }
        /// <summary>
        /// Gets or sets the value of CurrentPosition.
        /// </summary>
        [UANode(BrowsePath = ".Current_position"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public double CurrentPosition
            get { return currentPosition; }
            set { SetProperty(ref currentPosition, value); }
        /// <summary>
        /// Gets or sets the value of done.
        /// </summary>
        [UANode(BrowsePath = ".Done"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public bool Done
            get { return done; }
            set { SetProperty(ref done, value); }
        /// <summary>
        /// Gets or sets the value of Busy.
        /// </summary>
        [UANode(BrowsePath = ".Busy"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public bool Busy
            get { return busy; }
            set { SetProperty(ref busy, value); }
        /// <summary>
        /// Gets or sets the value of Error.
        /// </summary>
        [UANode(BrowsePath = ".Error"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public bool Error
            get { return error; }
            set { SetProperty(ref error, value); }
        /// <summary>
        /// Gets or sets the value of Error_code.
        /// </summary>
        [UANode(BrowsePath = ".Error_code"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public uint ErrorCode
            get { return errorCode; }
            set { SetProperty(ref errorCode, value); }
        /// <summary>
        /// Gets or sets the value of Write_digital_outputs.
        /// </summary>
        [UANode(BrowsePath = ".Write_digital_outputs"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public byte WriteDigitalOutputs
            get { return writeDigitalOutputs; }
            set { SetProperty(ref writeDigitalOutputs, value); }
        /// <summary>
        /// Gets or sets the value of Controlword.
        /// </summary>
        [UANode(BrowsePath = ".Controlword"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public ushort Controlword
            get { return controlword; }
            set { SetProperty(ref controlword, value); }
        /// <summary>
        /// Gets or sets the value of Target_pos.
        /// </summary>
        [UANode(BrowsePath = ".Target_pos"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public int TargetPos
            get { return targetPos; }
            set { SetProperty(ref targetPos, value); }
        /// <summary>
        /// Gets or sets the value of Mode_of_operation.
        /// </summary>
        [UANode(BrowsePath = ".Mode_of_operation"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public byte ModeOfOperation
            get { return modeOfOperation; }
            set { SetProperty(ref modeOfOperation, value); }
        /// <summary>
        /// Gets or sets the value of Digital_in.
        /// </summary>
        [UANode(BrowsePath = ".Digital_in"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public byte DigitalIn
            get { return digitalIn; }
            set { SetProperty(ref digitalIn, value); }
        /// <summary>
        /// Gets or sets the value of Digital_out.
        /// </summary>
        [UANode(BrowsePath = ".Digital_out"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public byte DigitalOut
            get { return digitalOut; }
            set { SetProperty(ref digitalOut, value); }
        /// <summary>
        /// Gets or sets the value of Analog_in.
        /// </summary>
        [UANode(BrowsePath = ".Analog_in"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public int AnalogIn
            get { return analogIn; }
            set { SetProperty(ref analogIn, value); }
        /// <summary>
        /// Gets or sets the value of Target_velocity.
        /// </summary>
        [UANode(BrowsePath = ".Target_velocity"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public int TargetVelocity
            get { return targetVelocity; }
            set { SetProperty(ref targetVelocity, value); }
        /// <summary>
        /// Gets or sets the value of Profile_velocity.
        /// </summary>
        [UANode(BrowsePath = ".Profile_velocity"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public int ProfileVelocity
            get { return profileVelocity; }
            set { SetProperty(ref profileVelocity, value); }
        /// <summary>
        /// Gets or sets the value of Actual_velocity.
        /// </summary>
        [UANode(BrowsePath = ".Actual_velocity"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public int ActualVelocity
            get { return actualVelocity; }
            set { SetProperty(ref actualVelocity, value); }
        /// <summary>
        /// Gets or sets the value of Statusword.
        /// </summary>
        [UANode(BrowsePath = ".Statusword"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public ushort Statusword
            get { return statusword; }
            set { SetProperty(ref statusword, value); }
        /// <summary>
        /// Gets or sets the value of Actual_pos.
        /// </summary>
        [UANode(BrowsePath = ".Actual_pos"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public int ActualPos
            get { return actualPos; }
            set { SetProperty(ref actualPos, value); }
        /// <summary>
        /// Gets or sets the value of Hw_errorcode.
        /// </summary>
        [UANode(BrowsePath = ".Hw_errorcode"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public short HwErrorcode
            get { return hwErrorcode; }
            set { SetProperty(ref hwErrorcode, value); }
        /// <summary>
        /// Gets or sets the value of Univar0.
        /// </summary>
        [UANode(BrowsePath = ".Univar0"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public int Univar0
            get { return univar0; }
            set { SetProperty(ref univar0, value); }
        /// <summary>
        /// Gets or sets the value of Univar1.
        /// </summary>
        [UANode(BrowsePath = ".UniVar1"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public int Univar1
            get { return univar1; }
            set { SetProperty(ref univar1, value); }
    [UAType]
    public class Meta : BindableBase
        #region private fields
        private bool available;
        private string fwVer;
        private string paramVer;
        private string fullName;
        private string enable;
        private string isEnabled;
        #endregion
        [UANode(BrowsePath = ".b_available"), UAData(Operations = UADataMappingOperations.ReadAndSubscribe, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public bool Available
            get { return available; }
            set { SetProperty(ref available, value); }
        [UANode(BrowsePath = ".fw_ver"), UAData(Operations = UADataMappingOperations.ReadAndSubscribe, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public string FwVer
            get { return fwVer; }
            set { SetProperty(ref fwVer, value); }
        [UANode(BrowsePath = ".param_ver"), UAData(Operations = UADataMappingOperations.ReadAndSubscribe, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public string ParamVer
            get { return paramVer; }
            set { SetProperty(ref paramVer, value); }
        [UANode(BrowsePath = ".full_name"), UAData(Operations = UADataMappingOperations.ReadAndSubscribe, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public string FullName
            get { return fullName; }
            set { SetProperty(ref fullName, value); }
        [UANode(BrowsePath = ".b_enable"), UAData(Operations = UADataMappingOperations.All, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public string Enable
            get { return enable; }
            set { SetProperty(ref enable, value); }
        [UANode(BrowsePath = ".b_is_enabled"), UAData(Operations = UADataMappingOperations.ReadAndSubscribe, Kind = UADataMappingKind.Value), UAMonitoring(SamplingInterval = 20), UASubscription(PublishingInterval = 200)]
        public string IsEnabled
            get { return isEnabled; }
            set { SetProperty(ref isEnabled, value); }
Time to create page: 0.071 seconds